-----BEGIN PGP SIGNED MESSAGE----- Hash: SHA256 Internap reporting via http://pastebin.com/9Fr2eW6U "The flooding has submerged and destroyed the site's diesel pumps and is preventing fuel from being pumped to the generators on the mezzanine level. The available fuel reserves on the mezzanine level are estimated to support customer loads for approximately 5-7 hours. Once this fuel supply has been exhausted the generator will no longer be able to sustain operation and critical customer power loads will be lost. The building itself is being evacuated and no remote hands support will be available to assist in any equipment shutdown." 75 Broad Street in Manhattan, where both Internap and Peer1 Hosting are shutting down operations. peer1 status page: http://forums.peer1.com/viewtopic.php?f=37&t=7532&p=9463%23p9463 regards, /virendra On 10/30/2012 09:59 AM, Martin Hepworth wrote:
Also reports AC2 transatlantic cable down and loss of connectivity to NY based servers. Along with reports on Ausnog about all the fun with the large DCs in Manhattan going to gennie power, diesel pumps being flooded and failing 'cos the tanks are in the basement...
Will be a massive clearup not just for the IT folks, Subways and road tunnels flooded so getting about will be challenging for a while.
_______________________________________________ Outages mailing list Outages@outages.org https://puck.nether.net/mailman/listinfo/outages